Hei

Finnes det krav til utførelse av jording mellom pipingflenser?

Eller bunner alt ut i målinger?

---

<div class="post-metadata">

**Author:** ![hans.olav.arnesen](https://avatars.discourse-cdn.com/v4/letter/h/dec6dc/32.png) [@hans.olav.arnesen](https://forum.trainor.no/u/hans.olav.arnesen)\
**Post date:** [april 8, 2024, 11:34am UTC](https://forum.trainor.no/t/jording-mellom-pipingflenser/585/2 "2024-04-08T11:34:00Z")

</div>

Om spørsmålet har relevans i henhold til Ex bør det adresseres i relevant forum for Ex.

NEK 400 beskriver ikke noe konkret krav relatert til temaet, men har generelle krav i avsnittene 411.3.1.2 og 444.5.