Hi
We have a cable 3x646AWG+3x4AWG. The line conductor is approximately 330 mm2 and the protective conductors are approximately 3x21,1mm2=63,3mm2.
According to IEC 60364-5-54 table 54.2 the protective conductors have to be half the size of the line conductor multiplied with a constant a: S*a/2. Is there any other rules or regulations to consider?
Can you say something about this constant a for this cable? Can we use this cable? Is the size of the protective conductors big enough?
Can this cable be used to supply a VFD controlled AC motor? Rated Voltage: 587 V, rated current: 1120 A.